residential fire sprinklers
The " house features" thread got me thinking about some of the things I have been considering for a new build... We will be building on an acreage about 10km from the nearest fire hall.
Anybody have a detached single family home with a sprinkler system? Good or bad? Cost?
ARG
__________________
In the immortal words of Jean Paul Sartre, 'Au revoir, gopher'.
Quote:
Originally Posted by sjemac
It has been scientifically proven that a 308 round will not leave your property -- they essentially fall dead at the fence line. But a 38 round, when fired from a handgun, will of its own accord leave your property and destroy any small schools nearby.
|
|
11-18-2018, 05:20 PM
|
|
|
|
Join Date: Oct 2008
Location: Cochrane AB
Posts: 894
|
|
I've seen them installed in a home probably about ten years ago and until the owner mentioned them (a sprinkler fitter), you would not even notice the head covers in the walls. Apparently his home insurance was substantially lower as well. With the going trend of building materials being used these days, I wouldn't be surprised to see them become a standard in new home construction.
|
11-18-2018, 05:52 PM
|
|
|
|
Join Date: Dec 2014
Posts: 798
|
|
This looks like a good idea.
Sent from my iPhone using Tapatalk
|
11-18-2018, 07:10 PM
|
Banned
|
|
Join Date: Aug 2012
Location: Calgary
Posts: 2,109
|
|
A fire suppression system isn't designed to extinguish the fire, just give you more time to evacuate should you need to. I guess answering the question if they're worth it comes down to how much you love your family, without sounding like to much of a ***** I hope. We have done without them for years but it's something that's becoming more standard and will be a part of the building code in the near future I would imagine.
Building a house with one, I believe it was about 8nuear to pay for it with the deduction in the insurance compared tk the same house without one. I'm not 100% on that number but that's what comes to mind after talking with our sprinkler rep.
|
11-18-2018, 08:52 PM
|
|
|
Join Date: Feb 2009
Posts: 339
|
|
I know in comerical/industrial you need a dedicated water supply for the sprinkler only (so nothing else can draw from it) if it’s not hooked up to a main water supply (ie. city grid). If residential has the same requirement it wouldn’t be worth considering.
|
11-18-2018, 09:55 PM
|
|
|
|
Join Date: Oct 2010
Location: central Alberta
Posts: 12,628
|
|
I posted this idea on another thread but will mention it here. I have seen this system on a log home surrounded by bush.
A external sprinkler system that wets a home down if a forest fire is close. A simple small diameter pipe that goes along the apex of the roof that trickles or mists the roof and house. Solar with battery power or a generator to run the pump.
__________________
___________________________________________
This country was started by voyagers whose young lives were swept away by the currents of the rivers for ten cents a day... just for the vanity of the European's beaver hats. ~ Red Bullets
___________________________________________
It is when you walk alone in nature that you discover your strengths and weaknesses. ~ Red Bullets
|
11-18-2018, 11:09 PM
|
|
|
Join Date: Aug 2015
Location: Alberta
Posts: 1,269
|
|
Quote:
Originally Posted by Red Bullets
I posted this idea on another thread but will mention it here. I have seen this system on a log home surrounded by bush.
A external sprinkler system that wets a home down if a forest fire is close. A simple small diameter pipe that goes along the apex of the roof that trickles or mists the roof and house. Solar with battery power or a generator to run the pump.
|
Noble idea - but no amount of misting is going to save a log cabin in the middle of a forest fire. Think that would have saved a log cabin from the beast in fort Mac ?? At best, it prolongs the inevitable.
|
11-19-2018, 01:05 AM
|
|
|
|
Join Date: Oct 2010
Location: central Alberta
Posts: 12,628
|
|
Quote:
Originally Posted by reddeerguy2015
Noble idea - but no amount of misting is going to save a log cabin in the middle of a forest fire. Think that would have saved a log cabin from the beast in fort Mac ?? At best, it prolongs the inevitable.
|
Maybe misting wouldn't be effective against a full out forest fire but a wet down roof would be less likely to ignite air born cinders. Might need a steady trickle flow to be effective.
__________________
___________________________________________
This country was started by voyagers whose young lives were swept away by the currents of the rivers for ten cents a day... just for the vanity of the European's beaver hats. ~ Red Bullets
___________________________________________
It is when you walk alone in nature that you discover your strengths and weaknesses. ~ Red Bullets
|
11-19-2018, 07:50 AM
|
|
|
Join Date: Sep 2012
Posts: 6,261
|
|
You need a enormous water supply and large piping for sprinkler system. Probably very hard to run pipe through walls and ceiling. In industry we often found the water was biggest hazard. Water falling on million dollar instrumentation caused more damage than the small fire.
|
11-19-2018, 07:11 PM
|
|
|
|
Join Date: Dec 2014
Posts: 798
|
|
Quote:
Originally Posted by Immigrant
This looks like a good idea.
Sent from my iPhone using Tapatalk
|
OOPS! I thought you ment for inside the house. For the outside I bought sprinklers from WASP http://www.waspwildfire.com/
They work pretty good. I tested them with a 400l/pm Honda high pressure pump. I plan to have 2 X 10,000l water tanks with 2 x pumps. My well pump will supplement the water tanks till the power goes out or the well (30" x 35feet deep) runs dry. Together with a tin roof it should buy me some time
|
11-19-2018, 07:58 PM
|
|
|
Join Date: Dec 2008
Posts: 2,600
|
|
Quote:
Originally Posted by reddeerguy2015
Noble idea - but no amount of misting is going to save a log cabin in the middle of a forest fire. Think that would have saved a log cabin from the beast in fort Mac ?? At best, it prolongs the inevitable.
|
The cabin might not be in the middle of the fire but wearing the roof will stop ignition from embers blown in.
|
11-19-2018, 08:05 PM
|
|
|
|
Join Date: May 2007
Posts: 452
|
|
Quote:
Originally Posted by Big Grey Wolf
You need a enormous water supply and large piping for sprinkler system. Probably very hard to run pipe through walls and ceiling. In industry we often found the water was biggest hazard. Water falling on million dollar instrumentation caused more damage than the small fire.
|
Actually you do not need large water supplies for residential fire sprinklers. It can be done with about 30 gpm at 50 psi. So a small tank(350 usgallons) by code a 10 minute water supply is all that is required and any csa approved pump would work. Cost would be about 4 to 5 dollars per square ft for an average home.
Now if your talking warehouse fire sprinklers 12 to 1500 usgpm, a diesel driven fire pump and large piping.
As far as having an accidental sprinkler head discharge 99% of the time it is the result of a poor installation.
|
11-20-2018, 08:40 AM
|
|
|
|
Join Date: Oct 2011
Location: Westerose
Posts: 4,057
|
|
Quote:
Originally Posted by Immigrant
This looks like a good idea.
Sent from my iPhone using Tapatalk
|
Those are interesting... thanks
Quote:
Originally Posted by Ronan_357
I know in comerical/industrial you need a dedicated water supply for the sprinkler only (so nothing else can draw from it) if it’s not hooked up to a main water supply (ie. city grid). If residential has the same requirement it wouldn’t be worth considering.
|
That is one of the things I'm trying to figure out. I have seen info that says a tank and pump "may" be required... what they don't say is how big a tank and what exactly "may" means.
Quote:
Originally Posted by Big Grey Wolf
You need a enormous water supply and large piping for sprinkler system. Probably very hard to run pipe through walls and ceiling. In industry we often found the water was biggest hazard. Water falling on million dollar instrumentation caused more damage than the small fire.
|
I know the large pipes aren't required for residential. Some system will work off the existing plumbing.
Quote:
Originally Posted by Immigrant
OOPS! I thought you ment for inside the house. For the outside I bought sprinklers from WASP http://www.waspwildfire.com/
They work pretty good. I tested them with a 400l/pm Honda high pressure pump. I plan to have 2 X 10,000l water tanks with 2 x pumps. My well pump will supplement the water tanks till the power goes out or the well (30" x 35feet deep) runs dry. Together with a tin roof it should buy me some time
|
Interior was what I meant, but all info is welcome at this point.
We are planning Hardy board siding and a metal roof to be some what fire resistant. I was thinking of roof sprinklers, but had not started looking at options yet.
ARG
__________________
In the immortal words of Jean Paul Sartre, 'Au revoir, gopher'.
Quote:
Originally Posted by sjemac
It has been scientifically proven that a 308 round will not leave your property -- they essentially fall dead at the fence line. But a 38 round, when fired from a handgun, will of its own accord leave your property and destroy any small schools nearby.
|
|
11-20-2018, 09:36 AM
|
|
|
|
Join Date: May 2007
Posts: 452
|
|
Quote:
Originally Posted by Dark
Actually you do not need large water supplies for residential fire sprinklers. It can be done with about 30 gpm at 50 psi. So a small tank(350 usgallons) by code a 10 minute water supply is all that is required and any csa approved pump would work. Cost would be about 4 to 5 dollars per square ft for an average home.
Now if your talking warehouse fire sprinklers 12 to 1500 usgpm, a diesel driven fire pump and large piping.
As far as having an accidental sprinkler head discharge 99% of the time it is the result of a poor installation.
|
Au revoir, Gopher
Perhaps you missed my post, my job for the past 34 years has been installing/designing fire sprinklers.
Any questions feel free to ask.
|
11-20-2018, 11:04 AM
|
|
|
Join Date: Dec 2008
Posts: 2,600
|
|
Quote:
Originally Posted by Dark
Au revoir, Gopher
Perhaps you missed my post, my job for the past 34 years has been installing/designing fire sprinklers.
Any questions feel free to ask.
|
Dark, I have heard that even in a large industrial fire it is rare that more than two sprinklers deploy and the fire is usually controlled before the fire department arrives.
Is that a correct statement?
Thanks,
|
11-20-2018, 11:49 AM
|
|
|
|
Join Date: May 2007
Posts: 452
|
|
Quote:
Originally Posted by Battle Rat
Dark, I have heard that even in a large industrial fire it is rare that more than two sprinklers deploy and the fire is usually controlled before the fire department arrives.
Is that a correct statement?
Thanks,
|
You are correct.
The statistics used to be 90% of fires are extinguished with one sprinkler 99% extinguished with 2 sprinklers.
This does not apply to high hazard buildings such as warehouse.
We recently had a fire in a group home. A tenant stood his mattress against a wall a lit it on fire.
This small home had a small tank and pump, the fire was extinguished completely by one sprinkler head. The tenants did not have to leave the home they just had to mop up some water. Prior to this fire they had another fire that was extinguished by the local fire department, the house had to be completely gutted and the tenants had to find other accommodations for 6 months
|
11-22-2018, 06:22 AM
|
|
|
|
Join Date: Oct 2011
Location: Westerose
Posts: 4,057
|
|
Quote:
Originally Posted by Dark
Au revoir, Gopher
Perhaps you missed my post, my job for the past 34 years has been installing/designing fire sprinklers.
Any questions feel free to ask.
|
Sorry Dark, I didn't see your post until after I made my last post... I blame my browser, but it could have been lack of coffee
Thanks for the info. I guess I need to figure out where I could put a water tank (the area set aside for mechanical is starting to get crowded) and if I can find another $5/sq ft in the budget.
ARG
__________________
In the immortal words of Jean Paul Sartre, 'Au revoir, gopher'.
Quote:
Originally Posted by sjemac
It has been scientifically proven that a 308 round will not leave your property -- they essentially fall dead at the fence line. But a 38 round, when fired from a handgun, will of its own accord leave your property and destroy any small schools nearby.
|
|
11-22-2018, 06:35 AM
|
|
|
|
Join Date: May 2007
Posts: 452
|
|
Quote:
Originally Posted by Au revoir, Gopher
Sorry Dark, I didn't see your post until after I made my last post... I blame my browser, but it could have been lack of coffee
Thanks for the info. I guess I need to figure out where I could put a water tank (the area set aside for mechanical is starting to get crowded) and if I can find another $5/sq ft in the budget.
ARG
|
I see you are from Calgary, I would get a few quotes from your local companies.
I work in the Edmonton area.
|