The "house features" thread got me thinking about some of the things I have been considering for a new build... We will be building on an acreage about 10km from the nearest fire hall.

Anybody have a detached single family home with a sprinkler system? Good or bad? Cost?

ARG
__________________
In the immortal words of Jean Paul Sartre, 'Au revoir, gopher'.

Quote:
Originally Posted by sjemac View Post
It has been scientifically proven that a 308 round will not leave your property -- they essentially fall dead at the fence line. But a 38 round, when fired from a handgun, will of its own accord leave your property and destroy any small schools nearby.
Reply With Quote
  #2  
Old 11-18-2018, 05:20 PM
kmacisaac's Avatar
kmacisaac kmacisaac is offline
 
Join Date: Oct 2008
Location: Cochrane AB
Posts: 894
Default

I've seen them installed in a home probably about ten years ago and until the owner mentioned them (a sprinkler fitter), you would not even notice the head covers in the walls. Apparently his home insurance was substantially lower as well. With the going trend of building materials being used these days, I wouldn't be surprised to see them become a standard in new home construction.
Reply With Quote
  #3  
Old 11-18-2018, 05:52 PM
Immigrant's Avatar
Immigrant Immigrant is offline
 
Join Date: Dec 2014
Posts: 798
Default

This looks like a good idea.






Sent from my iPhone using Tapatalk
Reply With Quote
  #4  
Old 11-18-2018, 07:10 PM
Scottmisfits Scottmisfits is offline
Banned
 
Join Date: Aug 2012
Location: Calgary
Posts: 2,109
Default

A fire suppression system isn't designed to extinguish the fire, just give you more time to evacuate should you need to. I guess answering the question if they're worth it comes down to how much you love your family, without sounding like to much of a ***** I hope. We have done without them for years but it's something that's becoming more standard and will be a part of the building code in the near future I would imagine.

Building a house with one, I believe it was about 8nuear to pay for it with the deduction in the insurance compared tk the same house without one. I'm not 100% on that number but that's what comes to mind after talking with our sprinkler rep.
Reply With Quote
  #5  
Old 11-18-2018, 08:52 PM
Ronan_357 Ronan_357 is offline
 
Join Date: Feb 2009
Posts: 339
Default

I know in comerical/industrial you need a dedicated water supply for the sprinkler only (so nothing else can draw from it) if it’s not hooked up to a main water supply (ie. city grid). If residential has the same requirement it wouldn’t be worth considering.
Reply With Quote
  #6  
Old 11-18-2018, 09:55 PM
Red Bullets's Avatar
Red Bullets Red Bullets is offline
 
Join Date: Oct 2010
Location: central Alberta
Posts: 12,628
Default

I posted this idea on another thread but will mention it here. I have seen this system on a log home surrounded by bush.
A external sprinkler system that wets a home down if a forest fire is close. A simple small diameter pipe that goes along the apex of the roof that trickles or mists the roof and house. Solar with battery power or a generator to run the pump.
__________________
___________________________________________
This country was started by voyagers whose young lives were swept away by the currents of the rivers for ten cents a day... just for the vanity of the European's beaver hats. ~ Red Bullets
___________________________________________
It is when you walk alone in nature that you discover your strengths and weaknesses. ~ Red Bullets
Reply With Quote
  #7  
Old 11-18-2018, 11:09 PM
reddeerguy2015 reddeerguy2015 is offline
 
Join Date: Aug 2015
Location: Alberta
Posts: 1,269
Default

Quote:
Originally Posted by Red Bullets View Post
I posted this idea on another thread but will mention it here. I have seen this system on a log home surrounded by bush.
A external sprinkler system that wets a home down if a forest fire is close. A simple small diameter pipe that goes along the apex of the roof that trickles or mists the roof and house. Solar with battery power or a generator to run the pump.
Noble idea - but no amount of misting is going to save a log cabin in the middle of a forest fire. Think that would have saved a log cabin from the beast in fort Mac ?? At best, it prolongs the inevitable.
Reply With Quote
  #8  
Old 11-19-2018, 01:05 AM
Red Bullets's Avatar
Red Bullets Red Bullets is offline
 
Join Date: Oct 2010
Location: central Alberta
Posts: 12,628
Default

Quote:
Originally Posted by reddeerguy2015 View Post
Noble idea - but no amount of misting is going to save a log cabin in the middle of a forest fire. Think that would have saved a log cabin from the beast in fort Mac ?? At best, it prolongs the inevitable.
Maybe misting wouldn't be effective against a full out forest fire but a wet down roof would be less likely to ignite air born cinders. Might need a steady trickle flow to be effective.
__________________
___________________________________________
This country was started by voyagers whose young lives were swept away by the currents of the rivers for ten cents a day... just for the vanity of the European's beaver hats. ~ Red Bullets
___________________________________________
It is when you walk alone in nature that you discover your strengths and weaknesses. ~ Red Bullets
Reply With Quote
  #9  
Old 11-19-2018, 07:50 AM
Big Grey Wolf Big Grey Wolf is offline
 
Join Date: Sep 2012
Posts: 6,261
Default

You need a enormous water supply and large piping for sprinkler system. Probably very hard to run pipe through walls and ceiling. In industry we often found the water was biggest hazard. Water falling on million dollar instrumentation caused more damage than the small fire.
Reply With Quote
  #10  
Old 11-19-2018, 07:11 PM
Immigrant's Avatar
Immigrant Immigrant is offline
 
Join Date: Dec 2014
Posts: 798
Default

Quote:
Originally Posted by Immigrant View Post
This looks like a good idea.






Sent from my iPhone using Tapatalk
OOPS! I thought you ment for inside the house. For the outside I bought sprinklers from WASP http://www.waspwildfire.com/
They work pretty good. I tested them with a 400l/pm Honda high pressure pump. I plan to have 2 X 10,000l water tanks with 2 x pumps. My well pump will supplement the water tanks till the power goes out or the well (30" x 35feet deep) runs dry. Together with a tin roof it should buy me some time
Reply With Quote
  #11  
Old 11-19-2018, 07:58 PM
Battle Rat Battle Rat is offline
 
Join Date: Dec 2008
Posts: 2,600
Default

Quote:
Originally Posted by reddeerguy2015 View Post
Noble idea - but no amount of misting is going to save a log cabin in the middle of a forest fire. Think that would have saved a log cabin from the beast in fort Mac ?? At best, it prolongs the inevitable.
The cabin might not be in the middle of the fire but wearing the roof will stop ignition from embers blown in.
Reply With Quote
  #12  
Old 11-19-2018, 08:05 PM
Dark's Avatar
Dark Dark is offline
 
Join Date: May 2007
Posts: 452
Smile

Quote:
Originally Posted by Big Grey Wolf View Post
You need a enormous water supply and large piping for sprinkler system. Probably very hard to run pipe through walls and ceiling. In industry we often found the water was biggest hazard. Water falling on million dollar instrumentation caused more damage than the small fire.
Actually you do not need large water supplies for residential fire sprinklers. It can be done with about 30 gpm at 50 psi. So a small tank(350 usgallons) by code a 10 minute water supply is all that is required and any csa approved pump would work. Cost would be about 4 to 5 dollars per square ft for an average home.

Now if your talking warehouse fire sprinklers 12 to 1500 usgpm, a diesel driven fire pump and large piping.

As far as having an accidental sprinkler head discharge 99% of the time it is the result of a poor installation.
Reply With Quote
  #13  
Old 11-20-2018, 08:40 AM
Au revoir, Gopher's Avatar
Au revoir, Gopher Au revoir, Gopher is offline
 
Join Date: Oct 2011
Location: Westerose
Posts: 4,057
Default

Quote:
Originally Posted by Immigrant View Post
This looks like a good idea.






Sent from my iPhone using Tapatalk
Those are interesting... thanks

Quote:
Originally Posted by Ronan_357 View Post
I know in comerical/industrial you need a dedicated water supply for the sprinkler only (so nothing else can draw from it) if it’s not hooked up to a main water supply (ie. city grid). If residential has the same requirement it wouldn’t be worth considering.
That is one of the things I'm trying to figure out. I have seen info that says a tank and pump "may" be required... what they don't say is how big a tank and what exactly "may" means.

Quote:
Originally Posted by Big Grey Wolf View Post
You need a enormous water supply and large piping for sprinkler system. Probably very hard to run pipe through walls and ceiling. In industry we often found the water was biggest hazard. Water falling on million dollar instrumentation caused more damage than the small fire.
I know the large pipes aren't required for residential. Some system will work off the existing plumbing.

Quote:
Originally Posted by Immigrant View Post
OOPS! I thought you ment for inside the house. For the outside I bought sprinklers from WASP http://www.waspwildfire.com/
They work pretty good. I tested them with a 400l/pm Honda high pressure pump. I plan to have 2 X 10,000l water tanks with 2 x pumps. My well pump will supplement the water tanks till the power goes out or the well (30" x 35feet deep) runs dry. Together with a tin roof it should buy me some time
Interior was what I meant, but all info is welcome at this point.

We are planning Hardy board siding and a metal roof to be some what fire resistant. I was thinking of roof sprinklers, but had not started looking at options yet.

ARG
__________________
In the immortal words of Jean Paul Sartre, 'Au revoir, gopher'.

Quote:
Originally Posted by sjemac View Post
It has been scientifically proven that a 308 round will not leave your property -- they essentially fall dead at the fence line. But a 38 round, when fired from a handgun, will of its own accord leave your property and destroy any small schools nearby.
Reply With Quote
  #14  
Old 11-20-2018, 09:36 AM
Dark's Avatar
Dark Dark is offline
 
Join Date: May 2007
Posts: 452
Default

Quote:
Originally Posted by Dark View Post
Actually you do not need large water supplies for residential fire sprinklers. It can be done with about 30 gpm at 50 psi. So a small tank(350 usgallons) by code a 10 minute water supply is all that is required and any csa approved pump would work. Cost would be about 4 to 5 dollars per square ft for an average home.

Now if your talking warehouse fire sprinklers 12 to 1500 usgpm, a diesel driven fire pump and large piping.

As far as having an accidental sprinkler head discharge 99% of the time it is the result of a poor installation.
Au revoir, Gopher

Perhaps you missed my post, my job for the past 34 years has been installing/designing fire sprinklers.
Any questions feel free to ask.
Reply With Quote
  #15  
Old 11-20-2018, 11:04 AM
Battle Rat Battle Rat is offline
 
Join Date: Dec 2008
Posts: 2,600
Default

Quote:
Originally Posted by Dark View Post
Au revoir, Gopher

Perhaps you missed my post, my job for the past 34 years has been installing/designing fire sprinklers.
Any questions feel free to ask.
Dark, I have heard that even in a large industrial fire it is rare that more than two sprinklers deploy and the fire is usually controlled before the fire department arrives.
Is that a correct statement?
Thanks,
Reply With Quote
  #16  
Old 11-20-2018, 11:49 AM
Dark's Avatar
Dark Dark is offline
 
Join Date: May 2007
Posts: 452
Default

Quote:
Originally Posted by Battle Rat View Post
Dark, I have heard that even in a large industrial fire it is rare that more than two sprinklers deploy and the fire is usually controlled before the fire department arrives.
Is that a correct statement?
Thanks,
You are correct.

The statistics used to be 90% of fires are extinguished with one sprinkler 99% extinguished with 2 sprinklers.
This does not apply to high hazard buildings such as warehouse.

We recently had a fire in a group home. A tenant stood his mattress against a wall a lit it on fire.
This small home had a small tank and pump, the fire was extinguished completely by one sprinkler head. The tenants did not have to leave the home they just had to mop up some water. Prior to this fire they had another fire that was extinguished by the local fire department, the house had to be completely gutted and the tenants had to find other accommodations for 6 months
Reply With Quote
  #17  
Old 11-22-2018, 06:22 AM
Au revoir, Gopher's Avatar
Au revoir, Gopher Au revoir, Gopher is offline
 
Join Date: Oct 2011
Location: Westerose
Posts: 4,057
Default

Quote:
Originally Posted by Dark View Post
Au revoir, Gopher

Perhaps you missed my post, my job for the past 34 years has been installing/designing fire sprinklers.
Any questions feel free to ask.
Sorry Dark, I didn't see your post until after I made my last post... I blame my browser, but it could have been lack of coffee

Thanks for the info. I guess I need to figure out where I could put a water tank (the area set aside for mechanical is starting to get crowded) and if I can find another $5/sq ft in the budget.

ARG
__________________
In the immortal words of Jean Paul Sartre, 'Au revoir, gopher'.

Quote:
Originally Posted by sjemac View Post
It has been scientifically proven that a 308 round will not leave your property -- they essentially fall dead at the fence line. But a 38 round, when fired from a handgun, will of its own accord leave your property and destroy any small schools nearby.
Reply With Quote
  #18  
Old 11-22-2018, 06:35 AM
Dark's Avatar
Dark Dark is offline
 
Join Date: May 2007
Posts: 452
Default

Quote:
Originally Posted by Au revoir, Gopher View Post
Sorry Dark, I didn't see your post until after I made my last post... I blame my browser, but it could have been lack of coffee

Thanks for the info. I guess I need to figure out where I could put a water tank (the area set aside for mechanical is starting to get crowded) and if I can find another $5/sq ft in the budget.

ARG
I see you are from Calgary, I would get a few quotes from your local companies.
I work in the Edmonton area.
Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT -6. The time now is 07:25 PM.


Powered by vBulletin® Version 3.8.5
Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.