Furnaces will not turn on
We had a power failure early today and now the furnaces (2) will not turn on ,checked breaker, and power supply and reset. still nothing any ideas!!
__________________
jpg images
LIFE IS TO SHORT TO HAVE AN UGLY LOOKIN DOG .....GET A LAB
|
01-16-2018, 08:22 PM
|
|
|
|
Join Date: Dec 2008
Location: Alberta
Posts: 24,071
|
|
Do you have and can you run a volt meter?
Can you remove the 2 wires from the thermostat and cross them at the furnace? That will tell you if it is the thermostat. It is basically an on off switch unless it is a 3 wire with cooling.
Just reread 2- are they on single or dual thermostats?
__________________
Only dead fish go with the flow. The rest use their brains in life.
Originally Posted by Twisted Canuck
I wasn't thinking far enough ahead for an outcome, I was ranting. By definition, a rant doesn't imply much forethought.....
|
01-16-2018, 08:22 PM
|
|
Moderator
|
|
Join Date: Feb 2015
Posts: 7,654
|
|
I don't know what type of furnace it is, but does it have a fuse?
|
01-16-2018, 08:23 PM
|
Banned
|
|
Join Date: Dec 2007
Location: Edmonton
Posts: 2,485
|
|
Quote:
Originally Posted by threeforthree
We had a power failure early today and now the furnaces (2) will not turn on ,checked breaker, and power supply and reset. still nothing any ideas!!
|
Is this a house or commercial building?
|
01-16-2018, 08:38 PM
|
|
|
|
Join Date: Mar 2011
Posts: 2,758
|
|
It's in a home no lights flashing on the see thru glass in furnaces they are York fuses look good
__________________
jpg images
LIFE IS TO SHORT TO HAVE AN UGLY LOOKIN DOG .....GET A LAB
|
01-16-2018, 08:39 PM
|
|
|
Join Date: May 2008
Location: The South
Posts: 1,128
|
|
Won’t turn on or won’t fire? Reg may need to be reset if it’s the latter (and an older reg)
|
01-16-2018, 08:42 PM
|
|
|
|
Join Date: Mar 2011
Posts: 2,758
|
|
Will not turn on
__________________
jpg images
LIFE IS TO SHORT TO HAVE AN UGLY LOOKIN DOG .....GET A LAB
|
01-16-2018, 08:48 PM
|
|
|
|
Join Date: Dec 2008
Location: Alberta
Posts: 24,071
|
|
where are you? Maybe someone on the board can help?
__________________
Only dead fish go with the flow. The rest use their brains in life.
Originally Posted by Twisted Canuck
I wasn't thinking far enough ahead for an outcome, I was ranting. By definition, a rant doesn't imply much forethought.....
|
01-16-2018, 08:51 PM
|
|
|
|
Join Date: Mar 2011
Posts: 2,758
|
|
Mer hat
__________________
jpg images
LIFE IS TO SHORT TO HAVE AN UGLY LOOKIN DOG .....GET A LAB
|
01-16-2018, 08:52 PM
|
|
|
|
Join Date: Mar 2011
Posts: 2,758
|
|
House is down to 16 wife no crying yet. Loll
__________________
jpg images
LIFE IS TO SHORT TO HAVE AN UGLY LOOKIN DOG .....GET A LAB
|
01-16-2018, 08:53 PM
|
|
|
|
Join Date: Mar 2011
Posts: 2,758
|
|
Both furnaces will not turn on
__________________
jpg images
LIFE IS TO SHORT TO HAVE AN UGLY LOOKIN DOG .....GET A LAB
|
01-16-2018, 08:55 PM
|
|
|
|
Join Date: Jan 2008
Location: Calgary Perchdance
Posts: 18,882
|
|
Take the furnace filters out. Replace after turning power back on. Make sure water coming out to drain is not backed up. Make sure vent to outside is not shut off. Turn breaker off to furnace and thermostat. Check thermostat is not set to air condition by accident.
__________________
It is not the most intellectual of the species that survives; it is not the strongest that survives; but the species that survives is the one that is able best to adapt and adjust to the changing environment in which it finds itself. Charles Darwin
|
01-16-2018, 08:58 PM
|
|
|
Join Date: Dec 2009
Posts: 1,309
|
|
Turn on your gas fireplace in the meantime, if you have one.
|
01-16-2018, 09:03 PM
|
|
|
|
Join Date: Apr 2010
Location: Communist Capital of Alberta
Posts: 3,768
|
|
High or mid efficiency.? Ie pilot or no pilot.
Is the bottom door back on to close the safety switch?
Did you try resetting the breaker?
There is a fuse on the board behind the lower door, but doubtful they both blew at the same time.
Thermostat: 1 for each or 1 for both?
If I was closer I'd come by, but if you can answer the above would help a lot.
|
01-16-2018, 09:06 PM
|
|
|
Join Date: Dec 2008
Location: Camrose
Posts: 45,128
|
|
Electronic thermostat or mechanical? So you have a voltage tester to verify voltage to the furnaces? Is there a reset on the furnaces.
__________________
Only accurate guns are interesting.
|
01-16-2018, 09:09 PM
|
|
|
|
Join Date: Oct 2008
Location: Cochrane AB
Posts: 894
|
|
Chances are if there was any type of surge, than the circuit board may be toast. I would also check the battery in the thermostat (if it requires one). It may be dead and not giving the call for heat when turned from off to the desired temperature. If there are no lights on inside the furnace my guess is the circuit board.
|
01-16-2018, 09:11 PM
|
|
|
Join Date: Jul 2015
Location: Calgary, AB
Posts: 1,022
|
|
Trace the electrical line coming out of the furnace back to the switch, turn it off - wait 5 seconds - turn back on.
Is your thermostat analog or digital ?
|
01-16-2018, 09:12 PM
|
|
|
|
Join Date: May 2007
Location: WMU 303
Posts: 8,493
|
|
|
01-16-2018, 09:14 PM
|
|
Moderator
|
|
Join Date: Jun 2010
Location: Stony Plain
Posts: 6,641
|
|
My furnace does this on occasion, Turn the thermostat to zero then turn the power switch off for the furnace. switch it back on and then set the thermostat.
|
01-16-2018, 09:15 PM
|
|
|
|
Join Date: Mar 2011
Posts: 2,758
|
|
Got it going thanks guys
Checked power at furnace and nothing went back to panel box and flicked it back and forth and they started,, will replace circuit in panel tomorrow...again thanks guys....wife can take her onezzy off tonight..
__________________
jpg images
LIFE IS TO SHORT TO HAVE AN UGLY LOOKIN DOG .....GET A LAB
|
01-16-2018, 09:21 PM
|
|
Moderator
|
|
Join Date: Jun 2010
Location: Stony Plain
Posts: 6,641
|
|
Quote:
Originally Posted by threeforthree
Checked power at furnace and nothing went back to panel box and flicked it back and forth and they started,, will replace circuit in panel tomorrow...again thanks guys....wife can take her onezzy off tonight..
|
|
01-16-2018, 09:27 PM
|
|
|
|
Join Date: Oct 2017
Location: Calgary-Red Deer area
Posts: 3,258
|
|
Clean the thermocouple with a piece of sand paper. Don't touch it with bare hands tho. It will leave oil deposits.
|
01-16-2018, 09:34 PM
|
|
|
|
Join Date: Apr 2010
Location: Communist Capital of Alberta
Posts: 3,768
|
|
Good to hear!
I just went through this with a York during that cold snap, except it wasn't the breaker.
Gotta say, I'll never buy a York. (And yes, I know brand had nothing to do with the problem. )
Stay warm!
|
01-16-2018, 09:52 PM
|
|
|
|
Join Date: Aug 2007
Location: Calgary
Posts: 19,419
|
|
Quote:
Originally Posted by Savage Bacon
Clean the thermocouple with a piece of sand paper. Don't touch it with bare hands tho. It will leave oil deposits.
|
Ignore this mans advice, its incorrect in at least three ways; even more depending on your type of furnace.
__________________
"The trouble with people idiot-proofing things, is the resulting evolution of the idiot." Me
|
01-16-2018, 10:28 PM
|
|
|
|
Join Date: Apr 2010
Location: Communist Capital of Alberta
Posts: 3,768
|
|
Now that I reread your last post, I find it odd that they ran both furnaces off of the same breaker....unless it's not a 15amp?
At 3x full load amps for start up on both motors you'd be way over 15 amps for a second or two. More like 40 to 60 amps depending on motor size.
I know the odds of them starting at the exact same time are astronomical, just surprised they used a common breaker.
|
01-16-2018, 10:34 PM
|
|
|
|
Join Date: Mar 2011
Posts: 2,758
|
|
Quote:
Originally Posted by CBintheNorth
Now that I reread your last post, I find it odd that they ran both furnaces off of the same breaker....unless it's not a 15amp?
At 3x full load amps for start up on both motors you'd be way over 15 amps for a second or two. More like 40 to 60 amps depending on motor size.
I know the odds of them starting at the exact same time are astronomical, just surprised they used a common breaker.
|
It is a double pole breaker
__________________
jpg images
LIFE IS TO SHORT TO HAVE AN UGLY LOOKIN DOG .....GET A LAB
|
01-16-2018, 10:57 PM
|
|
|
|
Join Date: Aug 2007
Location: Calgary
Posts: 19,419
|
|
Quote:
Originally Posted by threeforthree
It is a double pole breaker
|
They likely did this as both furnace power supplies are probably run into the same electrical box, its a safety thing as one does not want to shut off a breaker, then dive into the junction box and find there is still a live circuit in there. If each furnace had a separate junction box they could have individual breakers. If they're fed by a two 14/2 wires they can be split. If its a single 14/3 supplying both then it won't work without new wire pulled form the panel.
__________________
"The trouble with people idiot-proofing things, is the resulting evolution of the idiot." Me
|
01-17-2018, 06:21 AM
|
|
|
Join Date: May 2008
Location: The South
Posts: 1,128
|
|
Quote:
Originally Posted by Savage Bacon
Clean the thermocouple with a piece of sand paper. Don't touch it with bare hands tho. It will leave oil deposits.
|
Do not do this.
|
01-17-2018, 09:12 AM
|
|
|
|
Join Date: Aug 2007
Location: Calgary
Posts: 19,419
|
|
Quote:
Originally Posted by vinny
Do not do this.
|
Yup. It's either an intentional troll post or the guys got absolutely no clue of what a thermocouple even is. He may have been instructed incorrectly and that fault would be someone else's, but it's still wrong regardless. I could dip the business end of a thermocouple in a 4 liter jug of oil for a month and it would work fine. Not the electrical connection end mind you, but the part the flame impinges upon.
__________________
"The trouble with people idiot-proofing things, is the resulting evolution of the idiot." Me
|
01-17-2018, 09:27 AM
|
Banned
|
|
Join Date: Jun 2016
Posts: 3,666
|
|
I'd suggest anyone with these new furnaces have a spare mother board, igniter and vacuum switch on hand. The law of Murphy says that you're furnace will eff up on a Saturday night on the coldest day of the year.
|