Default Electrical sub panel

Yes, I know I should just hire an electrician but I'm cheap and poor
I want to put a sub panel in a detached garage, 100' away from the main panel
I will have a couple lighting circuits (15 amp) and 3-4 20 amp receptacles on two separate breakers.
I happen to have plenty of #10 3 conductor teck 90 cable on hand, as well as an unused 40 double pole breaker in my main panel.
Question is, can I get away using this breaker for my minimal load or should I buy a dbl 30 (which I believe is code?)




Sent from my iPhone using Tapatalk
Reply With Quote
  #2  
Old 03-26-2017, 10:39 AM
RancheroMan RancheroMan is offline
 
Join Date: May 2007
Location: Sherwood Park
Posts: 264
Default

*Not an Electrician*

Breakers are there to protect wire, not equipment. A 40amp breaker will allow to much current for #10 wire and could possibly cause excessive heating of the service wires (would you ever be in a situation where you are drawing all 40 amp, tough to say). I think a double pole breaker is around 20-30 bucks depending on your panel. Pretty cheap insurance.
Reply With Quote
  #3  
Old 03-26-2017, 10:43 AM
Dick284's Avatar
Dick284 Dick284 is offline
 
Join Date: May 2007
Location: Dreadful Valley
Posts: 14,620
Default

Hire an electrician, as there is far more to this than first appears.

Not to mention the permitting requirements, which can effect resale and insurance.
__________________


There are no absolutes
Reply With Quote
  #4  
Old 03-26-2017, 11:01 AM
wellpastcold wellpastcold is offline
 
Join Date: Apr 2012
Posts: 583
Default

As Dick suggested just hire an electrician. There are plenty around who would work with you. Dig your own trench. Drill the holes in the studs and do any of the other "grunt" work you can handle. Let them know you have the tech cable. Let a pro pull the permit and do the tie ins and wiring. You will be happy you did when you go to sell or if you ever had any kind of issues with your garage involving insurance.
Reply With Quote
  #5  
Old 03-26-2017, 11:44 AM
dodgeboy1979's Avatar
dodgeboy1979 dodgeboy1979 is offline
 
Join Date: Jul 2012
Location: Lloydminster Alberta
Posts: 1,298
Default

you can always pull the permit yourself, however you will be required to have it inspected. That's what i did for my garage. With a #10 wire you should be good for up to 30 amps.
Reply With Quote
  #6  
Old 03-26-2017, 12:03 PM
Alephnaught Alephnaught is offline
 
Join Date: Feb 2016
Posts: 133
Default

Totally DIY-able. From your post, you've got a fair bit of thinking & learning to do on this, but it's completely achievable. Pick up a copy of the CEC and a couple of DIY electrical manuals & do some reading. Then, draw up a plan for what you're gonna do & go in and grab a permit. Have the work inspected & off you go. These skills are totally learnble.
Reply With Quote
  #7  
Old 03-26-2017, 12:05 PM
Mountain Guy Mountain Guy is offline
 
Join Date: Apr 2008
Location: In the Rockies
Posts: 2,940
Default

You don't need an electrician to do that simple job....pull your own permit and just do it right.
Don't have my calculator handy but I'm thinking #10 might be a little undersized to go that distance @ 40A.
Reply With Quote
  #8  
Old 03-26-2017, 12:08 PM
roger's Avatar
roger roger is offline
 
Join Date: May 2007
Location: wmu 222, member #197
Posts: 4,907
Default

im not an electrician either and ive never played one on tv, with crime being what it is of late it wont be easier than being one wire or two.

i would suggest that run a length underground cat5 and/or a empty pvc conduit for security cam wiring, intercom, thermal controls and such.
also run NMWU 12/2 for the exterior lites so that when you turn on the house lites it turns on th eexterior lites on the garage as well.
if you plan on heating it one day you can run underground plastic gasline and steel gas risers too in the same trench.

you mentioned that your cheap but doing things twice isnt.
__________________
there are two kinds of people...those with loaded guns and those who dig.
the good, the bad, the ugly

weatherby fans clik here....
http://www.outdoorsmenforum.ca/group.php?groupid=31
Reply With Quote
  #9  
Old 03-26-2017, 02:05 PM
whiteout whiteout is offline
 
Join Date: Dec 2014
Posts: 940
Default

I did this exact thing this past summer, just with heavier gauge wire and bigger breakers.

You can easily do all the required work by yourself, from pulling the permit to doing the final terminations. The municipality will provide you with all the code information you need as well.

Where are you located?
Reply With Quote
  #10  
Old 03-26-2017, 05:37 PM
CBHurricane CBHurricane is offline
 
Join Date: Nov 2015
Posts: 24
Default

Pick up the CEC, #10 is only good for 30A. This calculation changes due to distance though as well, with codes being changed due to % loss limits.

Sent from my XP7700 using Tapatalk
Reply With Quote
  #11  
Old 03-26-2017, 07:22 PM
trophybook trophybook is offline
Banned
 
Join Date: Jan 2010
Location: West of the 5th
Posts: 954
Default

Go with#6 ALU and a 40 amp sub panel
Reply With Quote
  #12  
Old 03-26-2017, 07:34 PM
nick0danger nick0danger is offline
 
Join Date: Oct 2009
Location: Calgary
Posts: 1,507
Default

I'll check the IEC when I get home but I'm pretty sure the smallest wire to feed a panel is #8awg
Reply With Quote
  #13  
Old 03-26-2017, 07:41 PM
SteveY66's Avatar
SteveY66 SteveY66 is offline
 
Join Date: May 2007
Location: Edmonton
Posts: 661
Default

I'm a master electrician and you will need a new 2P 30 amp breaker as 40A is too large for that wire. Depending on how big your garage is and what equipment is present 30A is plenty.

However keep in mind most stand up compressors are 20A. I have a 32'x30' triple garage and I have a 60 amp sub panel installed.


Do it right pull a permit and have inspected
Reply With Quote
  #14  
Old 03-26-2017, 08:39 PM
Grizzly Adams's Avatar
Grizzly Adams Grizzly Adams is offline
 
Join Date: May 2007
Location: Central Alberta
Posts: 21,399
Default

Quote:
Originally Posted by SteveY66 View Post
I'm a master electrician and you will need a new 2P 30 amp breaker as 40A is too large for that wire. Depending on how big your garage is and what equipment is present 30A is plenty.

However keep in mind most stand up compressors are 20A. I have a 32'x30' triple garage and I have a 60 amp sub panel installed.


Do it right pull a permit and have inspected
No. 10 wire for a hundred foot run ?

Grizz
__________________
"Indeed, no human being has yet lived under conditions which, considering the prevailing climates of the past, can be regarded as normal."
John E. Pfeiffer The Emergence of Man
written in 1969
Reply With Quote
  #15  
Old 03-26-2017, 09:05 PM
Mountain Guy Mountain Guy is offline
 
Join Date: Apr 2008
Location: In the Rockies
Posts: 2,940
Default

Quote:
Originally Posted by Grizzly Adams View Post
No. 10 wire for a hundred foot run ?

Grizz
Sure why not..... light bulbs aren't as bright that way.
#2 AL minimum I'd say.
Reply With Quote
  #16  
Old 03-26-2017, 10:19 PM
canuck canuck is offline
 
Join Date: May 2007
Location: NW of Calgary
Posts: 437
Default

Thanks everyone for your info and even your opinions
As I thought, a 30 amp breaker is required for the #10 wire
Just to clarify, this is a simple vehicle storage structure and nothing more - it will have 6 lights and 2 (split) receptacles to plug block heaters into (likely no more than one at a time)
The power is being fed from my main shop where I do have the large demand (air compressor,welders,etc)
Reply With Quote
  #17  
Old 03-26-2017, 11:19 PM
SteveY66's Avatar
SteveY66 SteveY66 is offline
 
Join Date: May 2007
Location: Edmonton
Posts: 661
Default

Quote:
Originally Posted by Grizzly Adams View Post
No. 10 wire for a hundred foot run ?

Grizz
Yes don't be tricked. Breakers are set to trip at 80% of their rating for this case and residential. He is actually bringing 240 volt to the garage not 120 volt, hence why the 2 Pole breaker. See voltage drop values below.
Attached Images
File Type: jpg IMG_6928.jpg (16.8 KB, 61 views)
Reply With Quote
  #18  
Old 03-27-2017, 05:52 AM
canuck canuck is offline
 
Join Date: May 2007
Location: NW of Calgary
Posts: 437
Default

Quote:
Originally Posted by SteveY66 View Post
Yes don't be tricked. Breakers are set to trip at 80% of their rating for this case and residential. He is actually bringing 240 volt to the garage not 120 volt, hence why the 2 Pole breaker. See voltage drop values below.

Is that a phone app Steve?
Pretty cool, we use something similar to figure our min/max allowable pressures on a pressure factored (NG) meter set.
Thanks for your help.

Last edited by canuck; 03-27-2017 at 06:10 AM.
Reply With Quote
  #19  
Old 03-27-2017, 06:23 PM
Mountain Guy Mountain Guy is offline
 
Join Date: Apr 2008
Location: In the Rockies
Posts: 2,940
Default

Quote:
Originally Posted by SteveY66 View Post
Yes don't be tricked. Breakers are set to trip at 80% of their rating for this case and residential. He is actually bringing 240 volt to the garage not 120 volt, hence why the 2 Pole breaker. See voltage drop values below.
I'm not an electrician but I think Breakers are set to trip at rated amperage
Most breakers I've seen don't trip till 20% overloaded.
Are you referring to not being allowed to exceed 80% of the service size when calculating total load?.
Reply With Quote
  #20  
Old 03-29-2017, 05:12 PM
LSLAKER LSLAKER is offline
 
Join Date: Mar 2009
Posts: 241
Default

Quote:
Originally Posted by SteveY66 View Post
Yes don't be tricked. Breakers are set to trip at 80% of their rating for this case and residential. He is actually bringing 240 volt to the garage not 120 volt, hence why the 2 Pole breaker. See voltage drop values below.
He's not just bring 240 volts to the garage. He stated that he needs 120 volts for lighting and for the 120 volts receptacles. He will be installing a sub panel in the garage that will have both 240 volts and 120 volts. The 2 pole breaker will feed L1 and L2 to the sub panel.
L1 to L2 is 240 volts and either L1 or L2 to neutral (identified grounded conductor) is 120 volts.

If he stays within the loads that he has stated that he intends to place onto the sub panel he will be fine with #10 AWG conductors. Having split receptacles will share the 120 volt loads between L1 and L2 conductors.

Breakers are set to trip at their rating. If one knows the calculated load of the circuit then the load can not exceed 80%.

Last edited by LSLAKER; 03-29-2017 at 05:18 PM.
Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT -6. The time now is 06:55 PM.


Powered by vBulletin® Version 3.8.5
Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.