Default Furnaces will not turn on

We had a power failure early today and now the furnaces (2) will not turn on ,checked breaker, and power supply and reset. still nothing any ideas!!
__________________
jpg images

LIFE IS TO SHORT TO HAVE AN UGLY LOOKIN DOG .....GET A LAB
Reply With Quote
  #2  
Old 01-16-2018, 08:22 PM
Ken07AOVette's Avatar
Ken07AOVette Ken07AOVette is offline
 
Join Date: Dec 2008
Location: Alberta
Posts: 24,071
Default

Do you have and can you run a volt meter?

Can you remove the 2 wires from the thermostat and cross them at the furnace? That will tell you if it is the thermostat. It is basically an on off switch unless it is a 3 wire with cooling.

Just reread 2- are they on single or dual thermostats?
__________________
Only dead fish go with the flow. The rest use their brains in life.


Originally Posted by Twisted Canuck
I wasn't thinking far enough ahead for an outcome, I was ranting. By definition, a rant doesn't imply much forethought.....
Reply With Quote
  #3  
Old 01-16-2018, 08:22 PM
Trochu's Avatar
Trochu Trochu is offline
Moderator
 
Join Date: Feb 2015
Posts: 7,643
Default

I don't know what type of furnace it is, but does it have a fuse?
Reply With Quote
  #4  
Old 01-16-2018, 08:23 PM
Weedy1 Weedy1 is offline
Banned
 
Join Date: Dec 2007
Location: Edmonton
Posts: 2,485
Default

Quote:
Originally Posted by threeforthree View Post
We had a power failure early today and now the furnaces (2) will not turn on ,checked breaker, and power supply and reset. still nothing any ideas!!
Is this a house or commercial building?
Reply With Quote
  #5  
Old 01-16-2018, 08:38 PM
threeforthree's Avatar
threeforthree threeforthree is offline
 
Join Date: Mar 2011
Posts: 2,758
Default

It's in a home no lights flashing on the see thru glass in furnaces they are York fuses look good
__________________
jpg images

LIFE IS TO SHORT TO HAVE AN UGLY LOOKIN DOG .....GET A LAB
Reply With Quote
  #6  
Old 01-16-2018, 08:39 PM
vinny vinny is online now
 
Join Date: May 2008
Location: The South
Posts: 1,127
Default

Won’t turn on or won’t fire? Reg may need to be reset if it’s the latter (and an older reg)
Reply With Quote
  #7  
Old 01-16-2018, 08:42 PM
threeforthree's Avatar
threeforthree threeforthree is offline
 
Join Date: Mar 2011
Posts: 2,758
Default

Will not turn on
__________________
jpg images

LIFE IS TO SHORT TO HAVE AN UGLY LOOKIN DOG .....GET A LAB
Reply With Quote
  #8  
Old 01-16-2018, 08:48 PM
Ken07AOVette's Avatar
Ken07AOVette Ken07AOVette is offline
 
Join Date: Dec 2008
Location: Alberta
Posts: 24,071
Default

where are you? Maybe someone on the board can help?
__________________
Only dead fish go with the flow. The rest use their brains in life.


Originally Posted by Twisted Canuck
I wasn't thinking far enough ahead for an outcome, I was ranting. By definition, a rant doesn't imply much forethought.....
Reply With Quote
  #9  
Old 01-16-2018, 08:51 PM
threeforthree's Avatar
threeforthree threeforthree is offline
 
Join Date: Mar 2011
Posts: 2,758
Default

Mer hat
__________________
jpg images

LIFE IS TO SHORT TO HAVE AN UGLY LOOKIN DOG .....GET A LAB
Reply With Quote
  #10  
Old 01-16-2018, 08:52 PM
threeforthree's Avatar
threeforthree threeforthree is offline
 
Join Date: Mar 2011
Posts: 2,758
Default

House is down to 16 wife no crying yet. Loll
__________________
jpg images

LIFE IS TO SHORT TO HAVE AN UGLY LOOKIN DOG .....GET A LAB
Reply With Quote
  #11  
Old 01-16-2018, 08:53 PM
threeforthree's Avatar
threeforthree threeforthree is offline
 
Join Date: Mar 2011
Posts: 2,758
Default

Both furnaces will not turn on
__________________
jpg images

LIFE IS TO SHORT TO HAVE AN UGLY LOOKIN DOG .....GET A LAB
Reply With Quote
  #12  
Old 01-16-2018, 08:55 PM
Sundancefisher's Avatar
Sundancefisher Sundancefisher is offline
 
Join Date: Jan 2008
Location: Calgary Perchdance
Posts: 18,874
Default

Take the furnace filters out. Replace after turning power back on. Make sure water coming out to drain is not backed up. Make sure vent to outside is not shut off. Turn breaker off to furnace and thermostat. Check thermostat is not set to air condition by accident.
__________________
It is not the most intellectual of the species that survives; it is not the strongest that survives; but the species that survives is the one that is able best to adapt and adjust to the changing environment in which it finds itself. Charles Darwin
Reply With Quote
  #13  
Old 01-16-2018, 08:58 PM
propliner propliner is offline
 
Join Date: Dec 2009
Posts: 1,309
Default

Turn on your gas fireplace in the meantime, if you have one.
Reply With Quote
  #14  
Old 01-16-2018, 09:03 PM
CBintheNorth's Avatar
CBintheNorth CBintheNorth is offline
 
Join Date: Apr 2010
Location: Communist Capital of Alberta
Posts: 3,759
Default

High or mid efficiency.? Ie pilot or no pilot.
Is the bottom door back on to close the safety switch?
Did you try resetting the breaker?
There is a fuse on the board behind the lower door, but doubtful they both blew at the same time.
Thermostat: 1 for each or 1 for both?
If I was closer I'd come by, but if you can answer the above would help a lot.
Reply With Quote
  #15  
Old 01-16-2018, 09:06 PM
elkhunter11 elkhunter11 is online now
 
Join Date: Dec 2008
Location: Camrose
Posts: 45,112
Default

Electronic thermostat or mechanical? So you have a voltage tester to verify voltage to the furnaces? Is there a reset on the furnaces.
__________________
Only accurate guns are interesting.
Reply With Quote
  #16  
Old 01-16-2018, 09:09 PM
kmacisaac's Avatar
kmacisaac kmacisaac is offline
 
Join Date: Oct 2008
Location: Cochrane AB
Posts: 894
Default

Chances are if there was any type of surge, than the circuit board may be toast. I would also check the battery in the thermostat (if it requires one). It may be dead and not giving the call for heat when turned from off to the desired temperature. If there are no lights on inside the furnace my guess is the circuit board.
Reply With Quote
  #17  
Old 01-16-2018, 09:11 PM
FishOutOfWater FishOutOfWater is offline
 
Join Date: Jul 2015
Location: Calgary, AB
Posts: 1,021
Default

Trace the electrical line coming out of the furnace back to the switch, turn it off - wait 5 seconds - turn back on.
Is your thermostat analog or digital ?
Reply With Quote
  #18  
Old 01-16-2018, 09:12 PM
CNP's Avatar
CNP CNP is online now
 
Join Date: May 2007
Location: WMU 303
Posts: 8,494
Default

https://www.google.ca/search?q=furna...outage&ie=&oe=
Reply With Quote
  #19  
Old 01-16-2018, 09:14 PM
jungleboy's Avatar
jungleboy jungleboy is online now
Moderator
 
Join Date: Jun 2010
Location: Stony Plain
Posts: 6,633
Default

My furnace does this on occasion, Turn the thermostat to zero then turn the power switch off for the furnace. switch it back on and then set the thermostat.
Reply With Quote
  #20  
Old 01-16-2018, 09:15 PM
threeforthree's Avatar
threeforthree threeforthree is offline
 
Join Date: Mar 2011
Posts: 2,758
Default Got it going thanks guys

Checked power at furnace and nothing went back to panel box and flicked it back and forth and they started,, will replace circuit in panel tomorrow...again thanks guys....wife can take her onezzy off tonight..
__________________
jpg images

LIFE IS TO SHORT TO HAVE AN UGLY LOOKIN DOG .....GET A LAB
Reply With Quote
  #21  
Old 01-16-2018, 09:21 PM
jungleboy's Avatar
jungleboy jungleboy is online now
Moderator
 
Join Date: Jun 2010
Location: Stony Plain
Posts: 6,633
Default

Quote:
Originally Posted by threeforthree View Post
Checked power at furnace and nothing went back to panel box and flicked it back and forth and they started,, will replace circuit in panel tomorrow...again thanks guys....wife can take her onezzy off tonight..
Reply With Quote
  #22  
Old 01-16-2018, 09:27 PM
Savage Bacon's Avatar
Savage Bacon Savage Bacon is offline
 
Join Date: Oct 2017
Location: Calgary-Red Deer area
Posts: 3,253
Default

Clean the thermocouple with a piece of sand paper. Don't touch it with bare hands tho. It will leave oil deposits.
Reply With Quote
  #23  
Old 01-16-2018, 09:34 PM
CBintheNorth's Avatar
CBintheNorth CBintheNorth is offline
 
Join Date: Apr 2010
Location: Communist Capital of Alberta
Posts: 3,759
Default

Good to hear!
I just went through this with a York during that cold snap, except it wasn't the breaker.
Gotta say, I'll never buy a York. (And yes, I know brand had nothing to do with the problem.)

Stay warm!
Reply With Quote
  #24  
Old 01-16-2018, 09:52 PM
CaberTosser's Avatar
CaberTosser CaberTosser is offline
 
Join Date: Aug 2007
Location: Calgary
Posts: 19,418
Default

Quote:
Originally Posted by Savage Bacon View Post
Clean the thermocouple with a piece of sand paper. Don't touch it with bare hands tho. It will leave oil deposits.
Ignore this mans advice, its incorrect in at least three ways; even more depending on your type of furnace.
__________________
"The trouble with people idiot-proofing things, is the resulting evolution of the idiot." Me
Reply With Quote
  #25  
Old 01-16-2018, 10:28 PM
CBintheNorth's Avatar
CBintheNorth CBintheNorth is offline
 
Join Date: Apr 2010
Location: Communist Capital of Alberta
Posts: 3,759
Default

Now that I reread your last post, I find it odd that they ran both furnaces off of the same breaker....unless it's not a 15amp?
At 3x full load amps for start up on both motors you'd be way over 15 amps for a second or two. More like 40 to 60 amps depending on motor size.
I know the odds of them starting at the exact same time are astronomical, just surprised they used a common breaker.
Reply With Quote
  #26  
Old 01-16-2018, 10:34 PM
threeforthree's Avatar
threeforthree threeforthree is offline
 
Join Date: Mar 2011
Posts: 2,758
Default

Quote:
Originally Posted by CBintheNorth View Post
Now that I reread your last post, I find it odd that they ran both furnaces off of the same breaker....unless it's not a 15amp?
At 3x full load amps for start up on both motors you'd be way over 15 amps for a second or two. More like 40 to 60 amps depending on motor size.
I know the odds of them starting at the exact same time are astronomical, just surprised they used a common breaker.
It is a double pole breaker
__________________
jpg images

LIFE IS TO SHORT TO HAVE AN UGLY LOOKIN DOG .....GET A LAB
Reply With Quote
  #27  
Old 01-16-2018, 10:57 PM
CaberTosser's Avatar
CaberTosser CaberTosser is offline
 
Join Date: Aug 2007
Location: Calgary
Posts: 19,418
Default

Quote:
Originally Posted by threeforthree View Post
It is a double pole breaker
They likely did this as both furnace power supplies are probably run into the same electrical box, its a safety thing as one does not want to shut off a breaker, then dive into the junction box and find there is still a live circuit in there. If each furnace had a separate junction box they could have individual breakers. If they're fed by a two 14/2 wires they can be split. If its a single 14/3 supplying both then it won't work without new wire pulled form the panel.
__________________
"The trouble with people idiot-proofing things, is the resulting evolution of the idiot." Me
Reply With Quote
  #28  
Old 01-17-2018, 06:21 AM
vinny vinny is online now
 
Join Date: May 2008
Location: The South
Posts: 1,127
Default

Quote:
Originally Posted by Savage Bacon View Post
Clean the thermocouple with a piece of sand paper. Don't touch it with bare hands tho. It will leave oil deposits.
Do not do this.
Reply With Quote
  #29  
Old 01-17-2018, 09:12 AM
CaberTosser's Avatar
CaberTosser CaberTosser is offline
 
Join Date: Aug 2007
Location: Calgary
Posts: 19,418
Default

Quote:
Originally Posted by vinny View Post
Do not do this.
Yup. It's either an intentional troll post or the guys got absolutely no clue of what a thermocouple even is. He may have been instructed incorrectly and that fault would be someone else's, but it's still wrong regardless. I could dip the business end of a thermocouple in a 4 liter jug of oil for a month and it would work fine. Not the electrical connection end mind you, but the part the flame impinges upon.
__________________
"The trouble with people idiot-proofing things, is the resulting evolution of the idiot." Me
Reply With Quote
  #30  
Old 01-17-2018, 09:27 AM
Norwest Alta Norwest Alta is offline
Banned
 
Join Date: Jun 2016
Posts: 3,666
Default

I'd suggest anyone with these new furnaces have a spare mother board, igniter and vacuum switch on hand. The law of Murphy says that you're furnace will eff up on a Saturday night on the coldest day of the year.
Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT -6. The time now is 10:53 PM.


Powered by vBulletin® Version 3.8.5
Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.