Default overhead heater for new shop

I'm putting up a 2400sq ft shop and I'm wondering how many btu overhead furnace I would need. The shop will be fully insulated and I don't need it tropical in there. I've ruled out radiant heaters.

thanks in advance
Reply With Quote
  #2  
Old 05-24-2017, 06:26 AM
coreya3212 coreya3212 is offline
 
Join Date: Feb 2010
Location: Central Alberta
Posts: 2,984
Default

Quote:
Originally Posted by conan View Post
I'm putting up a 2400sq ft shop and I'm wondering how many btu overhead furnace I would need. The shop will be fully insulated and I don't need it tropical in there. I've ruled out radiant heaters.

thanks in advance
Volume counts. How high is the ceiling? Why have you ruled out radiant heaters?
Reply With Quote
  #3  
Old 05-24-2017, 06:45 AM
2011laramie 2011laramie is offline
 
Join Date: Sep 2014
Posts: 162
Default

Rough rule ive read is 40-50 btu/sq ft.

So that equals roughly 100000btu. Add efficiency loss, id shoot for a 120000btu/hr unit.

But a proper heat loss calc would yield a more precise answer.
Reply With Quote
  #4  
Old 05-24-2017, 07:49 AM
Don K's Avatar
Don K Don K is offline
 
Join Date: Oct 2011
Posts: 2,507
Default

Put in something larger than you need... Go with a Reznor 150,000 or equivalent. There's honestly next to no difference on the price of the heater when going from a 100-125k or 125-150k. You'll be happy that you can get a quicker recovery when you are trying to warm it up or reheat it on a cold day. It will basically burn the same amount of gas to heat the building, just quicker.
__________________
Life's too short to sweat the small stuff.
Aim Small = Miss Small
Reply With Quote
  #5  
Old 05-24-2017, 07:57 AM
t.tinsmith t.tinsmith is offline
 
Join Date: May 2014
Location: Elk Valley BC
Posts: 231
Default

Low intensity infra red tube heaters are the most economical to operate. A heat loss calc is a must to size the unit. Bigger is seldom better when this is done. These tube heaters don't require a band of temp rise to run well and you can operate them in any low temperature if you like without damaging them
Good luck
Reply With Quote
  #6  
Old 05-24-2017, 08:52 AM
conan conan is offline
 
Join Date: Nov 2007
Location: Edmonton
Posts: 495
Default

I will have 14 ft ceilings. I'm going to store a travel trailer in there and I thought radiant heater would get the trailer to warm
Reply With Quote
  #7  
Old 05-24-2017, 11:00 AM
Blastoff Blastoff is offline
 
Join Date: May 2009
Location: Canterbury
Posts: 1,316
Default

Put your trailer on the other wall. I second the radiant heater more efficient than over head or boiler
Reply With Quote
  #8  
Old 05-24-2017, 11:04 AM
conan conan is offline
 
Join Date: Nov 2007
Location: Edmonton
Posts: 495
Default

Quote:
Originally Posted by Blastoff View Post
Put your trailer on the other wall. I second the radiant heater more efficient than over head or boiler
Are the radiant s rated the same way in btu?
Reply With Quote
  #9  
Old 05-24-2017, 11:08 AM
Blastoff Blastoff is offline
 
Join Date: May 2009
Location: Canterbury
Posts: 1,316
Default

Quote:
Originally Posted by conan View Post
Are the radiant s rated the same way in btu?
I believe they are, but I am not a furnace guy.
Reply With Quote
  #10  
Old 05-24-2017, 11:09 AM
Blastoff Blastoff is offline
 
Join Date: May 2009
Location: Canterbury
Posts: 1,316
Default

Some one will chime in, but there is a distance vehicles should be parked away from the radiant tubes. Also the RV height should be around 11 feet high and if you leave room you will be fine.
Reply With Quote
  #11  
Old 05-24-2017, 01:19 PM
Knot Rite Knot Rite is offline
 
Join Date: Jul 2011
Location: Montana Rocky slopes/Alberta southern prairies
Posts: 361
Default

I had a Hot Dawg installed in my newly built man cave garage. Things got changed and the heater ended up near the t.v. Well that sucks.
Not sure how many BTU's it is but it can heat up B.U.T the size of a T.U.B.

Bobby
Reply With Quote
  #12  
Old 05-24-2017, 01:22 PM
skidderman skidderman is offline
 
Join Date: Dec 2009
Location: Spruce Grove, AB
Posts: 3,045
Default

I have the radiant heat and wish I had not done it.
Reply With Quote
  #13  
Old 05-24-2017, 03:02 PM
Stubb Stubb is offline
 
Join Date: Aug 2013
Posts: 383
Default

Also makes a difference on whether you are using spray foam insulation and leaving your trusses exposed or are you going to have a ceiling. If you have a ceiling and good r value id say you need a 150,000 unit. if you have the exposed roof and spray, you might need two 150's. I just finished a 1500 sq ft shop with 12' walls, insulated very well and went with one 125,000 BTU Reznor.
Reply With Quote
  #14  
Old 05-24-2017, 03:11 PM
conan conan is offline
 
Join Date: Nov 2007
Location: Edmonton
Posts: 495
Default

Quote:
Originally Posted by skidderman View Post
I have the radiant heat and wish I had not done it.
Why is that skidder?
Reply With Quote
  #15  
Old 05-24-2017, 03:28 PM
bat119's Avatar
bat119 bat119 is online now
 
Join Date: Jan 2012
Location: On the border in Lloydminster
Posts: 8,363
Default

I worked in a sheet metal shop with radiant heaters I didn't like the heat directly on me all the time sort of like working in the sun. Our shop had a 24' ceiling you could still feel heat when they came on, the worst was a heater directly over the shear and brake, we built a sheet metal umbrella for a shield.
__________________
Si vis pacem, para bellum
Reply With Quote
  #16  
Old 05-24-2017, 03:34 PM
Smokinyotes Smokinyotes is offline
 
Join Date: Jan 2013
Location: onoway, Ab
Posts: 6,982
Default

My shop is 2400 sq ftand i have a 150,000 btu tube heater works great
Reply With Quote
  #17  
Old 05-24-2017, 05:33 PM
skidderman skidderman is offline
 
Join Date: Dec 2009
Location: Spruce Grove, AB
Posts: 3,045
Default

Quote:
Originally Posted by conan View Post
Why is that skidder?
Too much heat focused in one area. Front of garage hot, back is cold. Can't leave my truck in because heater heats front of truck too much. A forced air would be more consistent and no concentrated heat. If my garage was higher I guess it might be better but not much. From my perspective it was a big mistake.
Reply With Quote
  #18  
Old 05-24-2017, 09:17 PM
liar liar is offline
 
Join Date: Feb 2010
Location: ft assiniboine area
Posts: 1,392
Default

Quote:
Originally Posted by skidderman View Post
Too much heat focused in one area. Front of garage hot, back is cold. Can't leave my truck in because heater heats front of truck too much. A forced air would be more consistent and no concentrated heat. If my garage was higher I guess it might be better but not much. From my perspective it was a big mistake.
my last garage had underslab heat and this one has overhead radiant . i am more than happy with the radiant heater . when i was shopping for it i talked to a lot of people and was told that a common mistake made is too big a heater ( industrial ) for too small a building ( residential )
Reply With Quote
  #19  
Old 05-24-2017, 09:55 PM
skidderman skidderman is offline
 
Join Date: Dec 2009
Location: Spruce Grove, AB
Posts: 3,045
Default

Quote:
Originally Posted by liar View Post
my last garage had underslab heat and this one has overhead radiant . i am more than happy with the radiant heater . when i was shopping for it i talked to a lot of people and was told that a common mistake made is too big a heater ( industrial ) for too small a building ( residential )
I could have too big a heater. I sized it according to charts but who knows. The other thing I could do is change the angle so it shoots further out. I may give that a try next fall.
Reply With Quote
  #20  
Old 05-25-2017, 07:27 AM
liar liar is offline
 
Join Date: Feb 2010
Location: ft assiniboine area
Posts: 1,392
Default

mine is a " calcana " . google it if you want . its been 5 winters and no issuses so far .
Reply With Quote
  #21  
Old 05-25-2017, 08:25 AM
Kale 19 Kale 19 is offline
 
Join Date: Feb 2008
Posts: 166
Default radiant heat

We built a 42'x60'x16' shop a few years back and installed 2, 75000 radiant heaters. Buddies of mine are gas fitters and we checked the specs and 1, 75000btu heater was enough for that shop. The shop is insulated with r25 in the walls and r60 in the ceiling and one heater is more than enough to keep it at 10C through the winter even on the coldest days. I installed the pair in the event one goes gown I have a backup. One gets set to 10C and the other at 8C. I do alternate from time to time to blow out any condensation. Remember that once your slab warms up, it will retain a lot of heat as well and help with recharge time. Only downside to the radiant tubes is that you will want to keep distance between them and your RV, at least 4-5ft.
We keep 2 fans running on low all the time and the shop stays at a very consistent temp. It was a bit more money to install 2 but when I'm away, I know the shop will (or should) always have a heat source. The peace of mind was worth the extra dough.
In floor would have been my first choice but at 20k more, I opted for the tubes and am very happy with them.
Reply With Quote
  #22  
Old 05-25-2017, 09:46 AM
FISHBATTEREDBEER FISHBATTEREDBEER is offline
Banned
 
Join Date: Dec 2016
Posts: 313
Default

Watch for big sales at Princess auto this time of yr on overhead units,I bought a Mr. Heater 80,000btu for just over $400 a few yrs ago,over 50% off.
Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT -6. The time now is 09:57 AM.


Powered by vBulletin® Version 3.8.5
Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.