Unhappy Detached Garage Insulation DIY failure!?!

Hey.

I need some advice/reassurance I haven't made a big insulation/vapour barrier mistake on my DIY project over the weekend.

Basically decided to insulate my detached 21X22ft garage as I use it as a home gym, and the Edmonton/Alberta winter is upon us.

I used basic batt insulation, and OSB boarding to make it a cheap and cheerful workable space in sub zero temperatures. My issue, I took advice for a garage cabinet guy in the US to determine the order to install materials.

His advice - External Wall/Vapour Barrier/Insulation/OSB.

Reading around (yes i probably should have done more prior) the general format for a house insulation is External Wall/Insulation/Vapour Barrier/Drywall.

Now. Should i be worried about moisture build up?

As it is a detached garage, I thought that the humidity/temperature variance inside to out probably won't vary too much and therefore minimal moisture build up.

Any advice would be greatly appreciated. I don't really want to rip it all down and start fresh!

Thanks
Reply With Quote
  #2  
Old 11-07-2016, 12:24 PM
Ken07AOVette's Avatar
Ken07AOVette Ken07AOVette is offline
 
Join Date: Dec 2008
Location: Alberta
Posts: 24,071
Default

I built my house and garage, you are right, the vapor barrier is the last thing you put up before interior sheeting or drywall.
Reply With Quote
  #3  
Old 11-07-2016, 12:27 PM
Desert_Faux's Avatar
Desert_Faux Desert_Faux is offline
 
Join Date: Aug 2010
Location: Leduc, Alberta
Posts: 238
Default

You dun goofed...
__________________
My posts are the intellectual property of the person commenting under the pseudonym "Desert_Faux". These posts are for informational and entertainment use only. Copying or quoting in whole, or in part, is given free license for use by any member of this board for use on this board. Any use, in whole or in part, for reference outside this forum requires the express written consent of its author.
Reply With Quote
  #4  
Old 11-07-2016, 12:31 PM
Austin's Avatar
Austin Austin is offline
 
Join Date: Jun 2007
Location: Edmonton SW
Posts: 1,565
Default

Insulation, vapor barrier, drywall or board

Not sure what part of the US he was from that would do it the order he suggested. You run the risk of where hot meets cold will create moisture -can form moisture and rot the exterior wall or insulation gets wet and sags or creates mold. You do not want mold
__________________
Reply With Quote
  #5  
Old 11-07-2016, 12:35 PM
bat119's Avatar
bat119 bat119 is online now
 
Join Date: Jan 2012
Location: On the border in Lloydminster
Posts: 8,358
Default

Is the space going to be heated 24/7 or just when you use it? I found turning the heat down to 10 C works better than shutting it off altogether that cement pad can take days to warm up again.
The vapour barrier goes on the warm side however where your at now I would run for the winter then check for moisture along the inside bottom of the walls in the spring.
__________________
Si vis pacem, para bellum
Reply With Quote
  #6  
Old 11-07-2016, 12:50 PM
Dick284's Avatar
Dick284 Dick284 is offline
 
Join Date: May 2007
Location: Dreadful Valley
Posts: 14,607
Default

Vapour barrier goes on the living side of the insulation.
Always.

Or better yet do it in spray foam and quite worrying.
__________________


There are no absolutes
Reply With Quote
  #7  
Old 11-07-2016, 12:51 PM
5ilver8ack16 5ilver8ack16 is offline
 
Join Date: Nov 2016
Posts: 7
Default

Bugger!

Ok. The space will be warmed gently when in use, I'm not planning on heating 24/7.

Options now...

1) Start Again
2) Wait and see worry about it in Spring if moisture is found.
3) Apply a second vapour barrier - creating vapour barrier on both sides of the insualtion.
4) Leave it, drink whiskey and try to forget about it!

Side note... I'm planning on applying for infill for the back yard, build a small 2-3 place on existing land... this will likely involved knocking down the garage and creating another building footprint in approx 3-4 years time.
Reply With Quote
  #8  
Old 11-07-2016, 12:57 PM
big zeke big zeke is online now
 
Join Date: Jul 2007
Posts: 1,075
Default Not that bad

The vapor barrier goes on the "warm in winter" side of the wall hence you have it backwards. You mention that you used OSB so taking it down shouldn't be too bad, much easier than if you used drywall and you can re-use the sheets.
My suggestion, take down the OSB one wall at a time, pull out the batts, tear out the vapor barrier that is against the outside walls (I'd be concerned that it could trap any moisture from the outside), then reinstall the batts, install the VB and screw the OSB in. If you do a wall a day you will be done later this week. If the labor is free, the total cost will be like $50 in VB and you'll be a lot smarter for the next time.
Make sure to Tuck tape any joints, the barrier has to be continuous.

Good Luck.
Zeke
Reply With Quote
  #9  
Old 11-07-2016, 01:51 PM
Bitumen Bullet Bitumen Bullet is offline
 
Join Date: May 2015
Posts: 418
Default

Quote:
Originally Posted by 5ilver8ack16 View Post
Bugger!

4) Leave it, drink whiskey and try to forget about it!

Side note... I'm planning on applying for infill for the back yard, build a small 2-3 place on existing land... this will likely involved knocking down the garage and creating another building footprint in approx 3-4 years time.
I like #4 but am pretty sure it's going to start getting moldy at some point so I'd be really sure about knocking down the garage in a few years before committing to it.

IMO Garages are the worst when it comes vapour barrier. We are told that the moisture barrier is on the outside and vapour barrier on the inside but that is really just the case for houses and areas that are heated 24/7.

If the area is not going to be heated all the time, or has other issues (dirt floor for example) then the vapour barrier becomes a bigger issue, moisture becomes a bigger issue, because it will be heated there will be moisture. Even unheated areas can have moisture problems, so it's always a concern.

If not #4 I would consider putting plastic on the inside, if I thought I could seal it completely and/or put a dehumidifier in there (can also double as a heater). Of course for the dehumidifier to work the place will have to be heated to around 10C (or something like that check instructions) but I have had some major success controlling moisture with cheap dehumidifiers and they are much easier to set up than trying to correct building issues in the winter.

Speaking of moisture control if I was trying to put that off until next year I would put some temperature probes in the wall by the vapour barrier, maybe even a hydrometer probe, in the faraway corner, down near the bottom of the wall. A cheap remote thermometer with external probe can be had for about $25. With temperature and humidify information you can determine how much of a problem condensation is going to be.

Another option is to put in a small cheap single pane window. Keep it free of condensation and chances are the walls will be fine.

BTW I think foam is the best but not if it is coming down in a few years.
Reply With Quote
  #10  
Old 11-07-2016, 02:09 PM
5ilver8ack16 5ilver8ack16 is offline
 
Join Date: Nov 2016
Posts: 7
Default

Thanks Bitumen Bullet!

I'm thinking #4 could be the best option. Failing that... Would I be causing more of an issue if i installed a 2nd vapour barrier behind the OSB.

Thus my setup would be...

External Wall/Vapour Barrier/Insulation/Vapour Barrier/OSB

Floor is still standard concrete slab.


Might be overkill... but seems like a good way to go, and not tear down a weekend of work...And with highly likely possibility of knockdown/property sale in maximum 5 years.

Honestly, we have been in the house 6 months and i haven't noticed any moisture issues in the garage... just bloody cold, so wanted to try warm it up for -40c and training in my garage gym.
Reply With Quote
  #11  
Old 11-07-2016, 02:41 PM
Clgy_Dave2.0 Clgy_Dave2.0 is offline
 
Join Date: Sep 2009
Location: Calgary
Posts: 4,962
Default

Quote:
Originally Posted by 5ilver8ack16 View Post
External Wall/Vapour Barrier/Insulation/Vapour Barrier/OSB...
= a "moisture sandwich".

That'd be worse than what you have currently.
Reply With Quote
  #12  
Old 11-07-2016, 02:51 PM
Moo Snukkle's Avatar
Moo Snukkle Moo Snukkle is offline
 
Join Date: Jul 2011
Location: Stony Plain
Posts: 1,144
Default

I'll take no insulation over dual vapour barrier (against code).
Reply With Quote
  #13  
Old 11-07-2016, 03:20 PM
Bitumen Bullet Bitumen Bullet is offline
 
Join Date: May 2015
Posts: 418
Default

Quote:
Originally Posted by 5ilver8ack16 View Post
Would I be causing more of an issue if i installed a 2nd vapour barrier behind the OSB.

Floor is still standard concrete slab.

Honestly, we have been in the house 6 months and i haven't noticed any moisture issues in the garage... just bloody cold, so wanted to try warm it up for -40c and training in my garage gym.
Add my name to the list thinking the moisture sandwich will be troublesome, actually I'm sure it will be, partially heated garages are not easy when it comes to moisture control. If you could actually seal the inside plastic (harder than it sounds) it might not be too bad for a few years but you would still want to monitor for moisture (maybe even vent) as it will get into the walls from the top, bottom and the many places not sealed during install.

By the time you notice moisture issues they can be huge and can cost a lot of money and effort.

I'd still go with #4, heat it, maybe dehumidifier, and then go back and do the job proper next summer. BTW you may be shocked at how much water damage occurs over that short time if you completely ignore the issue.

And when it comes to resale IMO you really should do it properly. Chances are you won't notice the moisture problems until a potential home buyer spots something or smells the mold. At that point you'll really wished you had fixed it when everything was new and not moldy. Mold can knock thousands off the price because the new buyer has to consider ripping everything down to studs and starting over with all new materials.
Reply With Quote
  #14  
Old 11-07-2016, 03:27 PM
pikergolf's Avatar
pikergolf pikergolf is offline
 
Join Date: Nov 2008
Posts: 11,338
Default

I wish people would speak to building inspectors. Free pertinent advice.
__________________
“One of the sad signs of our times is that we have demonized those who produce, subsidized those who refuse to produce, and canonized those who complain.”

Thomas Sowell
Reply With Quote
  #15  
Old 11-07-2016, 03:43 PM
Bitumen Bullet Bitumen Bullet is offline
 
Join Date: May 2015
Posts: 418
Default

Quote:
Originally Posted by pikergolf View Post
I wish people would speak to building inspectors. Free pertinent advice.
Yep, of course it's often it's like asking electricians about a specific grounding issue. "It's right here in the code book....." "Except for this exception here....". "The inspector in that area wants...." "We've always done it this way...". Fun to watch unless you are the one wanting an answer.


But in this case I'm betting most would say don't delay open it up and do it right. Which is pretty much the first answers given.
Reply With Quote
  #16  
Old 11-07-2016, 04:02 PM
Twisted Canuck's Avatar
Twisted Canuck Twisted Canuck is offline
 
Join Date: Jul 2009
Location: GP AB
Posts: 16,220
Default

You've heard it already, but you need to fix it. Simplest way to say it is vapor barrier goes on the warm side of the insulation. The way it is, you will have moisture issues, your insulation will get saturated regardless of how little you heat the space, and then you lose your R value and will have mold issues. DO NOT sandwich vapor barriers on both sides of insulation. Just asking for major moisture/mold issues. Best thing is tear the OSB off, pull out batts, take out Poly, and do it correctly. A huge pain in the butt, the alternative is worse. Just my two bits, but I would not leave it like that and hope for the best. In our climate, with such huge temperature swings season to season (+30 to -30 C) with a relatively high humidity in some seasons, you have to do it right.
__________________
'Once the monkeys learn they can vote themselves a banana, they'll never climb another tree.'. Robert Heinlein

'You can accomplish a lot more with a kind word and a gun, than with a kind word alone.' Al Capone
Reply With Quote
  #17  
Old 11-07-2016, 04:06 PM
TBD TBD is offline
Banned
 
Join Date: Sep 2008
Location: calgary, Alberta
Posts: 1,881
Default one other thing ...

depending on when that garage was built (at least in calgree anyways) the use of osb sheeting may not meet code. Something to check.

not good if you have a fire and try to collect insurance - I know I know - lots of details. welcome to the world of regulations.

I fear in the future it will be harder and harder (due to building codes and liability) for home owners to do these projects for themselves.
Reply With Quote
  #18  
Old 11-07-2016, 04:31 PM
Clgy_Dave2.0 Clgy_Dave2.0 is offline
 
Join Date: Sep 2009
Location: Calgary
Posts: 4,962
Default

Quote:
Originally Posted by TBD View Post
depending on when that garage was built (at least in calgree anyways) the use of osb sheeting may not meet code. Something to check.
Huh?

Source?
Reply With Quote
  #19  
Old 11-07-2016, 05:26 PM
Grizzly Adams's Avatar
Grizzly Adams Grizzly Adams is offline
 
Join Date: May 2007
Location: Central Alberta
Posts: 21,399
Default

Quote:
Originally Posted by pikergolf View Post
I wish people would speak to building inspectors. Free pertinent advice.
Any lumber yard employee would know this. In the old days they never worried about vapor barriers and the houses are still standing. Mistake was made, live with it.It's only a garage. Good coat of paint would cut down on moisture as well.

Grizz
__________________
"Indeed, no human being has yet lived under conditions which, considering the prevailing climates of the past, can be regarded as normal."
John E. Pfeiffer The Emergence of Man
written in 1969
Reply With Quote
  #20  
Old 11-07-2016, 06:14 PM
TBD TBD is offline
Banned
 
Join Date: Sep 2008
Location: calgary, Alberta
Posts: 1,881
Default yeh for garages built after a certain year ....

Quote:
Originally Posted by Clgy_Dave2.0 View Post
Huh?

Source?

Straight from the Safety Codes Officer...

AB Building Safety Codes
Article 9.35.4.1 Interior Finish
12.7mm thick gypsum board, or lathe and plaster conforming to subsection 9.29.4 or any material that can prevent the passage of flames when subjected to the standard fire exposure and CAN/ULC-S101. (fire endurance test of building construction or material)
So from that I guess you just need fireguard OSB to be good? Know parkland county for one does not allow OSB inside a garage, got a notice that a garage failed inspection, because owner put OSB inside.


I think it was 2010 .... not absolutely sure you'll need to do some research on this if you're not up to date

insurance companies are looking for absolutely any reason they can come up with to deny you insurance these days.

I know if it was my garage, factoring in how much I have invested in tools, I would make doubly sure interior osb finishing is allowed by code in my area.


.

Last edited by TBD; 11-07-2016 at 06:21 PM.
Reply With Quote
  #21  
Old 11-07-2016, 06:42 PM
Clgy_Dave2.0 Clgy_Dave2.0 is offline
 
Join Date: Sep 2009
Location: Calgary
Posts: 4,962
Default

Quote:
Originally Posted by TBD View Post
Straight from the Safety Codes Officer...

AB Building Safety Codes
Article 9.35.4.1 Interior Finish
12.7mm thick gypsum board, or lathe and plaster conforming to subsection 9.29.4 or any material that can prevent the passage of flames when subjected to the standard fire exposure and CAN/ULC-S101. (fire endurance test of building construction or material)
So from that I guess you just need fireguard OSB to be good? Know parkland county for one does not allow OSB inside a garage, got a notice that a garage failed inspection, because owner put OSB inside.


I think it was 2010 .... not absolutely sure you'll need to do some research on this if you're not up to date

insurance companies are looking for absolutely any reason they can come up with to deny you insurance these days.

I know if it was my garage, factoring in how much I have invested in tools, I would make doubly sure interior osb finishing is allowed by code in my area.


.
That's code for an attached garage (Or, IIRC, a detached garage with a dwelling above it). OP has a detached garage.


Quote:
The walls and ceilings of an attached garage shall have an
interior finish consisting of
a) not less than 12.7 mm thick gypsum board
conforming to Subsection 9.29.5.,
b) lath and plaster conforming to Subsection 9.29.4., or
c) any material that can be shown to remain in place
and prevent the passage of flames for not less than
15 min when subjected to the standard fire exposure
in CAN/ULC-S101, “Fire Endurance Tests of
Building Construction and Materials.”
Reply With Quote
  #22  
Old 11-07-2016, 06:42 PM
220 Swift 220 Swift is offline
 
Join Date: May 2007
Location: SE, Saskatchewan
Posts: 671
Default

If you find it getting damp an exhaust fan could be installed to pull moisture from inside. This is the actual purpose of a bathroom fan not just for farts.
Reply With Quote
  #23  
Old 11-07-2016, 06:45 PM
TBD TBD is offline
Banned
 
Join Date: Sep 2008
Location: calgary, Alberta
Posts: 1,881
Default oh ok ....

Quote:
Originally Posted by Clgy_Dave2.0 View Post
That's code for an attached garage (Or, IIRC, a detached garage with a dwelling above it). OP has a detached garage.
yeh my garage was attached, missed that.


thanks Dave !



PS ... dodged a bullet there silverback
Reply With Quote
  #24  
Old 11-07-2016, 08:29 PM
tiger woods tiger woods is offline
 
Join Date: Jun 2011
Posts: 122
Default

Quote:
Originally Posted by Twisted Canuck View Post
You've heard it already, but you need to fix it. Simplest way to say it is vapor barrier goes on the warm side of the insulation. The way it is, you will have moisture issues, your insulation will get saturated regardless of how little you heat the space, and then you lose your R value and will have mold issues. DO NOT sandwich vapor barriers on both sides of insulation. Just asking for major moisture/mold issues. Best thing is tear the OSB off, pull out batts, take out Poly, and do it correctly. A huge pain in the butt, the alternative is worse. Just my two bits, but I would not leave it like that and hope for the best. In our climate, with such huge temperature swings season to season (+30 to -30 C) with a relatively high humidity in some seasons, you have to do it right.
To the OP, sometimes trying to weed through the advice on an open forum like this can be difficult with all of the opinions that get thrown about.

This gentleman has nailed it for you. If there is one reply that you take into consideration, it should be this one.

The science behind it has to do with wherein the dew point lies within your roof or wall system, which will change depending on the outdoor and indoor temperatures. That's the coles notes version anyways.

Long story short, double vapour barrier is a no go. As is leaving it and hoping for the best. Unfortunately, if you want an insulated garage then you will have to do everything again, this time with the vapour barrier on the warm side (interior side) of the insulation. Wish I had a less labour intensive answer, but I can promise you that if you do it this way then you won't have to do it a third time.
Reply With Quote
  #25  
Old 11-07-2016, 09:25 PM
wildwoods wildwoods is offline
 
Join Date: Oct 2008
Location: Location
Posts: 4,961
Default

Quote:
Originally Posted by tiger woods View Post
To the OP, sometimes trying to weed through the advice on an open forum like this can be difficult with all of the opinions that get thrown about.

This gentleman has nailed it for you. If there is one reply that you take into consideration, it should be this one.

The science behind it has to do with wherein the dew point lies within your roof or wall system, which will change depending on the outdoor and indoor temperatures. That's the coles notes version anyways.

Long story short, double vapour barrier is a no go. As is leaving it and hoping for the best. Unfortunately, if you want an insulated garage then you will have to do everything again, this time with the vapour barrier on the warm side (interior side) of the insulation. Wish I had a less labour intensive answer, but I can promise you that if you do it this way then you won't have to do it a third time.
x3 listen to this advise.
I'm wondering how the heck you got the poly on BEFORE insulating in the first place...
But yes, please don't chance it. Don't double vapour barrier it (huge moisture trap). Tear it out and do it again. There will be some very inexpensive labour to have if you look hard enough. Perhaps hiring a handyman for a day will ease the pain of re-doing it all on your lonesome...
Way to swallow the pride and ask though. There's value in that.
Reply With Quote
  #26  
Old 11-07-2016, 09:26 PM
wildwoods wildwoods is offline
 
Join Date: Oct 2008
Location: Location
Posts: 4,961
Default

Quote:
Originally Posted by Clgy_Dave2.0 View Post
= a "moisture sandwich".

That'd be worse than what you have currently.
Quote:
Originally Posted by Moo Snukkle View Post
I'll take no insulation over dual vapour barrier (against code).
this^^^^
Reply With Quote
  #27  
Old 11-08-2016, 06:51 AM
Grizzly Adams's Avatar
Grizzly Adams Grizzly Adams is offline
 
Join Date: May 2007
Location: Central Alberta
Posts: 21,399
Default

Quote:
Originally Posted by TBD View Post
yeh my garage was attached, missed that.


thanks Dave !



PS ... dodged a bullet there silverback
Not a garage anymore either, it's a Man Cave.

Grizz
__________________
"Indeed, no human being has yet lived under conditions which, considering the prevailing climates of the past, can be regarded as normal."
John E. Pfeiffer The Emergence of Man
written in 1969
Reply With Quote
  #28  
Old 11-08-2016, 07:41 AM
elkhunter11 elkhunter11 is online now
 
Join Date: Dec 2008
Location: Camrose
Posts: 45,082
Default

Invest some labor now and redo the insulation/vapor barrier properly, or do it later while likely having to deal with a mold issue. The weather is nice now, don't waste it trying to avoid doing what you know you need to do.
__________________
Only accurate guns are interesting.
Reply With Quote
  #29  
Old 11-08-2016, 09:17 AM
Kim473's Avatar
Kim473 Kim473 is offline
 
Join Date: Jan 2010
Location: Edmonton
Posts: 6,470
Default

Vapor barrier always to the warm side. Redo it now while it's warm.
__________________
Kim

Gonna get me a 16" perch.
Reply With Quote
  #30  
Old 11-08-2016, 09:27 AM
HyperMOA HyperMOA is offline
 
Join Date: Feb 2012
Location: Edmonton (shudder)
Posts: 4,630
Default

This is why I am so scared to buy anything used. So you put a grand of insulation up, and do the job incorrectly. Just to save a few bucks. Which I can understand. Then instead of making the effort to resolve the issue you say you will likely sell it in 5 years. At that point you will want the realtor to reflect the price of an insulated garage. The new owner then has to tear down the walls and replace all the insulation. Have mold abatement done. Then they have to pay to dispose of the materials. Then they have to buy new insulation and vapour barrier. Then they have to install or pay for it to be installed. All of this for something they already paid you for!!! Tear it down and do it right. Next time you DIY make sure you know what to do.

It must've been really fun vapour barriering around all of those studs. At that point you should've stopped and realized how dumb the process was. Once you do it the right way you will see how really easy it should be.
Reply With Quote
Reply

Tags
edmonton, garage, garage plans, insulation

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT -6. The time now is 02:35 PM.


Powered by vBulletin® Version 3.8.5
Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.